Can Britain keep the grid stable without big power stations?

Coal, gas and nuclear stations kept the grid stable as a by-product of making power. Their spinning mass slows a fall in frequency after a fault, they pour out the surge of current that lets protection find the faulty line, and they hold voltage. Wind, solar and batteries do little of this unless built to. As the big stations close, NESO buys these services separately: £328m and £323m in its first two stability tenders.

One reading: the problem is in hand. NESO ran the grid at 97.7% clean power for a short period in 2025, and says new frequency services have let it lower the minimum inertia “while still increasing system security”. Another: NESO’s own research says the last-resort scheme, which cuts blocks of customers automatically when frequency falls, does “not take into account the growth of distributed generation and decreasing system inertia”.

Which is nearer the truth, and what evidence would settle it? Engineers who have worked on this are especially welcome.

1 Like

Over perhaps 20 years there have been progressive changes in the UK grid connected load which have combined to reduce grid stability quite apart from the changes in the generation technology caused by the renewables transition. The push for energy efficiency and the de -industrialization due to net zero have both reduced the number of direct on line asynchronous machines in use in UK industry . The use of inverters to power these motors can improve process efficiency by allowing speed optimization but it also effectively decouples their mechanical inertia from providing grid stability as their dynamic load no longer responds with negative feedback to grid frequency variation. The large number of these direct coupled machines found in a the uk industrial economy of years ago provided a distributed inertia to the grid which is being / has been lost.

It is of course possible to replace some of this inertia by suitable control of the existing inverter drives in continuous load high mechanical inertia applications ( such as large fans and blowers) but it is probable that improving connected load stability would simply mean politicians allowing renewables to reduce theirs giving no tangible benefit.

3 Likes

Welcome, Axon, and thank you. Nobody had raised the demand side, and it matters. NESO still assumes demand falls about 2.5% for every 1Hz drop in frequency (its charging methodology uses that figure), and much of that came from motors like the ones you describe. Do you know of anyone who has measured how far it has fallen? And on fans and blowers: has any site you know of been asked, or paid, to give that inertia back?

1 Like

As an electronic engineer, I find the inverter process between renewables and the grid odd. If the grid is required to be stable in frequency then the renewable inverters should simulate the mass of the spinning generators. While I do not know the specifics, the converter frequency should be controlled to be close to 50Hz with similar dynamics to the spinning resources, slightly lowering the frequency/phase under high load and increasing the frequency/phase under low load. I suspect that the inverter is simply allowed to free run under the control of the grid. It seems obvious that this is a poor policy when the spinning resources become close to zero.

1 Like

Hi Richard

My background is as a technical director of companies which have provided numerous engine and vehicle test systems around the world. These systems are highly dynamic and typically use regenerative rotating machines to absorb power (generally up to a few MW max) and often using grid power to simulate the physical inertia of a coupled vehicle under test.

I am therefore not familiar with Grid systems in general and can’t answer Richard’s very reasonable questions.

I would however point out that a first order proportional load relationship ( ie 2.5%/Hz) implies a grid with a significant proportion of DOL machines whose load is roughly linearly speed dependent. While DOL fans, blowers and pumps may have a higher dependency, inverter driven devices programmed with a constant speed set-point will not exhibit any such effect nor will they respond to voltage change on the line side.

My earlier point was really more to do with load change due to rate of frequency change ( ie dw/dt) which occurs in all DOL rotating machines due to the combined mechanical inertia of the machine and its coupled load. The machine and load will see a significant initial reduction in slip following a step change in line frequency causing a dynamic change in its electrical load which reduces as it approaches the new line frequency. This dynamic negative feedback is lost when inverter technology is used in place of a DOL system.

I have also worked on large battery simulators for EV’s and built high power electrical heating systems (hundreds of kW) and of course these devices, because of their modern electronic load control, may also fail to provide negative feedback with line supply voltage unless intentionally designed to do so.

My point is that concentrating stability effort entirely on the grid generators overlooks the fact that an entirely electronically controlled load side will not respond to the traditional grid voltage and frequency changes which provided natural stability in the past.

Instead high levels of overload need to be present at all times BOTH in generation and absorption.

.

Hello, really enjoyed the book. Hope many more people read it. Wanted to ask, those advocating the net zero transition imagine a circular economy, where goods are recycled, waste tips mined for metals, etc. thereby reducing need for carbon feedstocks - is this baloney? If so why?

IIRC in a recent FOI response to Kathryn Porter NESO said a 3% voltage reduction results in a 1.5% demand reduction, which they claim to have tested - but not in very appropriate test conditions. Of course, inverter based motors simply draw more current if the voltage drops. If they would get back to providing more inertia data we might be able to estimate the demand side. I’ve been meaning to try to run regressions between their published GVAs data and demand and levels of generation per type which might unearth the assumptions they are using (though not verifying them!). But it takes clean data with no glitches to do that: there are too many of them to make it a simple task.